wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Yep, that's what 215.2(A)(1)(a) says. And I'm questioning whether it's necessary. What's the hazard with 100A continuous load / 115A conductor ampacity / 125A breaker?with 100 amp continuous load minimum conductor ampacity must be 125%.
Cheers, Wayne