We are adding 8 enphase micros to a existing 14 micros with a existing 20 amp backfeed breaker wire size 10 AWG. The system will have 22 micros at 19.8 Amps 1.25=24.75 Amps.The plans call for 40 AMP backfeed breaker with 10 AWG, Feeding a solar subpanel with a 15 Amp and 20 Amp Solar CKTS,I'm I missing something 10 AWG on a 40 AMP breaker, Is there a Exception like the air conditioning,should I just change that 40 to a 25 or 30 Amp,thanks