We are adding 8 enphase micros to a existing 14 micros with a existing 20 amp backfeed breaker wire size 10 AWG. The system will have 22 micros at 19.8 Amps 1.25=24.75 Amps.The plans call for 40 AMP backfeed breaker with 10 AWG, Feeding a solar subpanel with a 15 Amp and 20 Amp Solar CKTS,I'm I missing something 10 AWG on a 40 AMP breaker, Is there a Exception like the air conditioning,should I just change that 40 to a 25 or 30 Amp,thanks
Under some conditions of use a #10 is adequately protected by a 40A breaker, but why? 22 Enphase 215's will fit into a 30A breaker.
So I ask again, why use a 40A breaker when a 30A breaker would suffice?Notwithstanding the ampacity listed in 310.15, 240.4(D)(7) puts a 30A OCPD max on 10awg cu. Inverter outputs are not among the uses permitted to follow other rules.