22 enphase micro invert

Status
Not open for further replies.

SAP

Senior Member
Location
Fresno Ca
The branch CKT's are 14 micros on a 20Amp, 8 micros on a 15 Amp located in a solar sub panel on the roof,there is no 22 micros on one branch CKT
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
We are adding 8 enphase micros to a existing 14 micros with a existing 20 amp backfeed breaker wire size 10 AWG. The system will have 22 micros at 19.8 Amps 1.25=24.75 Amps.The plans call for 40 AMP backfeed breaker with 10 AWG, Feeding a solar subpanel with a 15 Amp and 20 Amp Solar CKTS,I'm I missing something 10 AWG on a 40 AMP breaker, Is there a Exception like the air conditioning,should I just change that 40 to a 25 or 30 Amp,thanks

Under some conditions of use a #10 is adequately protected by a 40A breaker, but why? 22 Enphase 215's will fit into a 30A breaker.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Under some conditions of use a #10 is adequately protected by a 40A breaker, but why? 22 Enphase 215's will fit into a 30A breaker.

Notwithstanding the ampacity listed in 310.15, 240.4(D)(7) puts a 30A OCPD max on 10awg cu. Inverter outputs are not among the uses permitted to follow other rules.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Notwithstanding the ampacity listed in 310.15, 240.4(D)(7) puts a 30A OCPD max on 10awg cu. Inverter outputs are not among the uses permitted to follow other rules.
So I ask again, why use a 40A breaker when a 30A breaker would suffice?
 