Fred B
Senior Member
- Location
- Upstate, NY
- Occupation
- Electrician
Found this when I was finally able to get underneath a mess of wires in a 12x15x6 inch metal junction. The single 12awg wire is how they all were bonded back to main panel buss.There are also a few feeds that are Crimp fitted and then tied to this bundle. Think they ran out of room under the split. Is this a violation? I was thinking it would be better adding a ground buss bar and bond back with an 8awg. Any thoughts.
Grounding junction
The j box before I started.

I'm basically pulling all apart as the original (assuming unskilled person) that ran these when splitting the NM cut almost every conductor, some cut the entire 12 inch length of the conductor. This box connects between the main panel and a relay switch panel. Also found mixed neutral connections that don't connect like circuit neutrals to like circuits. Finding sliced conductors in main panel as well. Could the slices simply have opened over time and may not have been visible when it was first installed? Or failing (opening up) from heating due to the original insulation damage?
This is an old installation, not sure of last modification but original installation was early 1970s late 1960s so no AFCI. I'm changing a couple of circuits and rewire so will need AFCI on those. Not sure of impact on AFCI functioning with use of the GE RR7 relays, as all switching is done by relay switching and contactors.
Breaker panel is an old Westinghouse 40 space full with multiple double taps and a couple of tandem breakers. I think the Eaton BR is an acceptable new breaker for the now obsolete Westinghouse panel. Eaton makes a short body AFCI breaker that will help out given the crowded panel .
Grounding junction

The j box before I started.

I'm basically pulling all apart as the original (assuming unskilled person) that ran these when splitting the NM cut almost every conductor, some cut the entire 12 inch length of the conductor. This box connects between the main panel and a relay switch panel. Also found mixed neutral connections that don't connect like circuit neutrals to like circuits. Finding sliced conductors in main panel as well. Could the slices simply have opened over time and may not have been visible when it was first installed? Or failing (opening up) from heating due to the original insulation damage?
This is an old installation, not sure of last modification but original installation was early 1970s late 1960s so no AFCI. I'm changing a couple of circuits and rewire so will need AFCI on those. Not sure of impact on AFCI functioning with use of the GE RR7 relays, as all switching is done by relay switching and contactors.
Breaker panel is an old Westinghouse 40 space full with multiple double taps and a couple of tandem breakers. I think the Eaton BR is an acceptable new breaker for the now obsolete Westinghouse panel. Eaton makes a short body AFCI breaker that will help out given the crowded panel .