I have an issue with a jurisdiction in VA on a job we are working on for the number of receptacles on a 15 AMP circuit. They have no local amendments that give a requirement in a dwelling unit. The circuits are configured in a way to comply with 210.11(A). It is the second floor of a single family home.
It is 1282 sq.ft. using table 220.12 to compute the lighting load at 3va/sq.ft I get 3846 VA divide that by 120V and get 32.05A. This would lead me to believe that as long as I have at a minimum 3 - 15A general lighting circuits for this floor I am code compliant. We have met these requirements. Now it says NOWHERE that there is a maximum quantity of receptacles that can go on one of these circuits in a dwelling unit. The job was failed due to having 12 duplex on a circuit, in the bedrooms.
I am not looking for any of the general rule of thumb answers. I would like a code article that I don't think exists as to why he would be telling me 10 per circuit, especially when 220.14 doesn't apply to Dwelling units.
It is 1282 sq.ft. using table 220.12 to compute the lighting load at 3va/sq.ft I get 3846 VA divide that by 120V and get 32.05A. This would lead me to believe that as long as I have at a minimum 3 - 15A general lighting circuits for this floor I am code compliant. We have met these requirements. Now it says NOWHERE that there is a maximum quantity of receptacles that can go on one of these circuits in a dwelling unit. The job was failed due to having 12 duplex on a circuit, in the bedrooms.
I am not looking for any of the general rule of thumb answers. I would like a code article that I don't think exists as to why he would be telling me 10 per circuit, especially when 220.14 doesn't apply to Dwelling units.