mdshunk
- Right here.
220.14(D) requires a branch circuit to be calculated with the maximum value of the lamps that can be permissably installed for each fixture.
The UL Marking Guide does require that each recessed fixture have the maximum lamp labeled in the fixture. The UL Marking Guide also requires each trim to have the maximum lamp that may be installed noted on the trim, or the fixture to have a table inside that indicates maximum lamp sizes with respect to the possible trims.
[FONT=Arial,Bold]
[/FONT]
Question is... when sizing lighting circuits in accordance with 220.14(D), are we to consider the maximum lamp possible with any possible trim, or the maximum lamp possible with the present (or specified) trim? Is the rough-in section by itself the "luminaire"? Or, is the combination of the rough-in section and the trim the "luminaire"? Reason I question this, is because another note in the UL Marking Guide seems to indicate that the aggregate fixture might be both pieces, just installed in two parts:
[FONT=Arial,Bold]63. ROUGH-IN AND FINISHING SECTIONS [/FONT]— Some recessed luminaires are intended to be installedin two parts. The Rough-In Section usually consists of the plaster frame and junction box, and is marked “ROUGH-IN SECTION FOR USE WITH FINISHING SECTION __________”, or ROUGH-IN SECTION ____FOR CONVERTIBLE RECESSED LUMINAIRE.” The blanks are replaced by catalog numbers or series designations. The Finishing Section usually consists of the recessed housing and trim; it is marked with the manufacturer’s identification and catalogue number. A convertible recessed luminaire trim/finishing section is also marked “FINISHING-SECTION FOR USE WITH ROUGH-IN SECTION __________.” The blanks are replaced by the catalog number or series designations. If a light diffuser is not provided, an additional marking on the finishing section indicates that the luminaire must not be used with a light diffuser.
[FONT=Arial,Bold]
72. RECESSED LUMINAIRE LAMP REPLACEMENT MARKINGS
[/FONT][FONT=Arial,Bold][/FONT]
— Recessed luminaire housing or rough-in section may employ a marking system where the lamp replacement marking is dependent upon the trim or finishing section used. A luminaire housing is marked “USE ONLY WITH [Manufacturer] [Catalog Number] TRIMS”. A rough-in section is marked “ROUGH-IN SECTION FOR USE WITH FINISHING SECTION ______”. The blanks are filled in with manufacturer and trim or finishing section number as appropriate. All recessed luminaries are marked for lamp replacement “CAUTION – RISK OF FIRE. MAX ___ WATTS ___ TYPE”. A recessed luminaire that requires a different lamp wattage or type for an alternate trim or finishing section is marked “CAUTION – RISK OF FIRE” and a table specifying the trim or finishing section and the maximum lamp wattage and type permitted for use with it. Alternately the lamp replacement information can be included on the trim or finishing section. The lamp replacement markings can be concealed providing the trim or finishing section must be removed for relamping or it is additionally marked where visible during relamping “SEE OTHER (BACK) SIDE FOR RELAMPING INFORMATION.”