General lighting load includes everything except for fixed appliances.
You still must have a minimum of 2 SABC's, a laundry circuit (unless not required like multifamily with other laundry facilities), and a 20 amp bathroom circuit. But there is no additional load calculation for the bathroom it just needs to be on the 20 amp circuit, you could put 1000 receptacles on it plus lighting and are code compliant. The bathroom load is included in the general lighting @ 3VA/SF. You could also run 10 circuits to the bathroom and the load calculation is still 3 VA/SF.
I disagree in regards to what I was saying because 220.14(J) includes recepts from 210.52(E) and (G) not (D) which is the bathroom receptacles. BRANCH load calculations still have to be accounted for on the bath recepts, and if the feeder calcs don't have to be, then that is just another pointer as to the incongruity of this, as Charlie calls it circular references.