220/380 volt 50 HZ

Status
Not open for further replies.

Randy R

New member
I am in the US where our voltage is 120/208v or 277/480v 3 phase. In Europe the voltage is 220/380v or 240/415v 3 phase. In both cases the lower voltage is the square root of the higher voltage three phase. So in the US 120v is one phase to nuetral or ground. In Europe is 220v one phase to nuetral or ground as well, or is it two hots?
 
Randy R said:
I am in the US where our voltage is 120/208v or 277/480v 3 phase. In Europe the voltage is 220/380v or 240/415v 3 phase. In both cases the lower voltage is the square root of the higher voltage three phase. So in the US 120v is one phase to nuetral or ground. In Europe is 220v one phase to nuetral or ground as well, or is it two hots?


It is 220 phase to neutral or ground. 380 phase to phase.
When we first started exporting buildings that was the hardest thing to make everyone understand.
 
I'll just add that the neutral and " earth " wires do not tie together anywhere

in the system, and each 220v circuit has it's own neutral.
 
As an aside:
There may be a time when we start to see 415 L-L & 240V L-N here in the US, in an effort to reduce losses in transformers at large corporate computer/data processing buildings.
Many large data centers have server power supplies that can accept a range as high as 240V L-N (take a look at your own PC too), since they are manufactured to sell in Europe too without modification.
If the output of the UPS (uninterruptible power supply) is set at 415/240V, then there is no need for the PDU (power distribution unit) transformer and an instant increase in efficiency of 2% and less floor space taken up by transformers.
 
In most 220v-only places, there is only a single line conductor and the grounded conductor, unless the loads are large enough to require line-to-line voltage. Thing of a single leg from a 3-phase Y system. The panel has a single breaker-stab bus.
 
The 120/240 single phase / split phase thing is unique to the USA, Canada, and... I think thats it.

If you buy a European voltage UPS these days it'll be 400/230 output, as Europe is theroetically harmonized on the "Eurovolt" now. So in the UK the data centres with UPSs built in the last decade run on 230V, but if you switch the UPS to bypass the output voltage rises to 240V, as thats what the utility supplies...
 