I am supporting the design for a large hotel. The calculated service load is very close to pushing us up from a 5000 amp board to the next standard size of 6000 amps, and we really don’t want to go there.
Table 220.42 (applicable to lighting loads) gives us more generous demand factors than does Table 220.44 (applicable to receptacle loads). The Handbook Commentary that follows article 220.44 says that we can combine the receptacle load with the lighting load, and use the demand factors of Table 220.42. (Actually, the Commentary points us to Table 220.12, but I think that is a typo.) I don’t quite see that in the words of the article.
For receptacle load in non-dwelling units, I have always used the “100% of the first 10K and 50% of the rest” rule. Can I take the 50/40/30 rule that applies to hotel lighting loads, and use to for the receptacles as well? If so, can I take the further step of adding the lighting to the receptacles, before applying the 50/40/30 rule? For this project, it would give us another 200 amps of margin below the 5000 amp service size.
Table 220.42 (applicable to lighting loads) gives us more generous demand factors than does Table 220.44 (applicable to receptacle loads). The Handbook Commentary that follows article 220.44 says that we can combine the receptacle load with the lighting load, and use the demand factors of Table 220.42. (Actually, the Commentary points us to Table 220.12, but I think that is a typo.) I don’t quite see that in the words of the article.
For receptacle load in non-dwelling units, I have always used the “100% of the first 10K and 50% of the rest” rule. Can I take the 50/40/30 rule that applies to hotel lighting loads, and use to for the receptacles as well? If so, can I take the further step of adding the lighting to the receptacles, before applying the 50/40/30 rule? For this project, it would give us another 200 amps of margin below the 5000 amp service size.