You are required to use section 220.12. All that is required is the volt-ampere per square foot value be equal or greater than the value required by Table 220.12.I read it again, and I agree. Table 220.42 applies to the general lighting load, regardless if its calculated from the connected load, or the table 220.12. That makes more sense.
So how does one calculate the guest room receptacle load when you are using the total connected lighting load? If we were using table 220.12, we wouldn't have to count them at all per 220.12 (J).
But we are using the total connected lighting load, not table 220.12. It seems like we should have to add something for the guest room receptacles. I
t sounds like Charlie is using 180VA per duplex, and in that case it seems like he can definitely use the demand factors in table 220.42.
The rest falls in place per NEC design.