OK Ive asked a similar question here before and got only one response.I will further my question with a larger area and see if I can get it clear in my head . When using 220.44 to apply demand factor derates to receptacles loads am I not correct when I say you can not apply them to loads that are not calculated by 180 VA per outlet as in H and I,
or to be more frank you can not derate loads in J and K . unless you use 180 VA.
For instance if a question asked for the receptacle load for a 2000sq ft office
I would answer 2000 x 3.5 x 1.25 or 8750VA I cannot derate this further as 220.44 does not apply here.
And if this is so why do all of Mike Holts 2005 Masters exam prep questions have the derate in them. I have missed them time and time again because I don't derate when not 180va is this right or wrong. I need to know this the correct way and want advice now as to which is correct
For instance if a question asked for the receptacle load for a 2000sq ft office
I would answer 2000 x 3.5 x 1.25 or 8750VA I cannot derate this further as 220.44 does not apply here.
And if this is so why do all of Mike Holts 2005 Masters exam prep questions have the derate in them. I have missed them time and time again because I don't derate when not 180va is this right or wrong. I need to know this the correct way and want advice now as to which is correct