jwelectric
- North Carolina
These have already been sent but though I would post them here for comment.
1. Section and Paragraph:
220.52 (A)
2. Proposal Recommends:
X revised text
3. Proposal
Small Appliance Circuit Load. In each dwelling unit, the load shall be calculated at 1500 volt-amperes for each 2-wire small-appliance branch circuit ?re-qu-ir-ed- installed by 210.11(C)(1).
4. Statement of Problem and Substantiation for Proposal:
As worded it could be misunderstood that only two circuits are to be used in the service or feeder calculation due to the fact that 210.11 (C) (1) could lead one to believe that only two circuits are required by the wording ?two or more?. By changing the word required to installed it would make it clear that any and all circuits being installed as outlined by 210.11 (C)(1) would be required to be included in the service or feeder calculation.
See attached statements from inspectors and contractors from around the nation.
And
220.52 (B)
X revised text
3. Proposal
Laundry Circuit Load. A load of not less than 1500 volt-amperes shall be included for each 2-wire laundry branch circuit installed as ?re-qu-ir-ed- installed by 210.11(C)(2).
As worded it could be misunderstood that only one circuit is to be used in the service or feeder calculation due to the fact that 210.11 (C) (2) could lead one to believe that only one circuit is required by the wording ?at least one additional?. By changing the word required to installed it would make it clear that any and all circuits being installed as outlined by 210.11 (C)(2) would be required to be included in the service or feeder calculation.
I attached this insert from the NEC Handbook:
Using the information found in the National Electrical Code Handbook published by the National Fire Protection Association following 220.52 (B) as outlined below I base my belief that the word ?EACH? means to include all in the service and feeder calculation.
I copied and pasted this entire site.
220.52 (A)
X revised text
3. Proposal
And
220.52 (B)
X revised text
3. Proposal
Attached to each proposal is the following post from this site:from NEC Handbook
?In each dwelling unit, the feeder load is required to be calculated at 1500 volt-amperes for each of the two or more (2-wire) small-appliance branch circuits and at 1500 volt-amperes for each (2-wire) laundry branch circuit. Where additional small-appliance and laundry branch circuits are provided, they also are calculated at 1500 volt-amperes per circuit. These loads are permitted to be totaled and then added to the general lighting load. The demand factors in Table 220.42 can then be applied to the combined total load of the small-appliance branch circuits, the laundry branch circuit, and the general lighting from Table 220.12.?