charlie b said:
Help me understand. Which version of the handbook are you using, and where is the sample problem that you are discussing? I need to read their solution, in order to figure out what they are saying.
Don't mean to butt in but this is the example shown in the 2008 NECH
220.53 Appliance Load ? Dwelling Unit(s).
It shall be permissible to apply a demand factor of 75 percent to the nameplate rating load of four or more appliances fastened in place, other than electric ranges, clothes dryers, space-heating equipment, or air-conditioning equipment, that are served by the same feeder or service in a one-family, two-family, or multifamily dwelling.
For appliances fastened in place (other than ranges, clothes dryers, and space-heating and air-conditioning equipment), feeder capacity must be provided for the sum of these loads; for a total load of four or more such appliances, a demand factor of 75 percent may be applied. See Table 430.248 for the full-load current, in amperes, for single-phase ac motors, in accordance with 220.50.
Calculation Example
Determine the feeder capacity needed for a 120/240-volt fastened-in-place appliance load in a dwelling unit for the following:
Appliance Rating Load
Water heater 4000 W, 240 V 4000 VA
Kitchen disposal 1/2 hp, 120 V 1176 VA
Dishwasher 1200 W, 120 V 1200 VA
Furnace motor 1/4 hp, 120 V 696 VA
Attic fan 1/4 hp, 120 V 696 VA
Water pump 1/2 hp, 240 V 1176 VA
Solution
STEP 1.
Calculate the total of the six fastened-in-place appliances:
Total load = 4000VA + 1176 Va + 1200 VA
+696 VA + 696 VA + 1176 VA
=8944 VA
STEP 2.
Because the load is for more than four appliances, apply a demand factor of 75 percent:
8944 VA X 0.75 = 6708 VA
Thus, 6708 volt-amperes is the load to be added to the other determined loads for calculating the size of service and feeder conductors.