The other day I saw a 16KW range (240V) on a 40A circuit.
#8/3 NMB, 40A breaker.
I did the calculation according to 220.55 Note 1, and the installation seems to be code compliant.
8KW + (20% of 8KW) = 9.6 KW = 40.0A @ 240V
Is this correct?
It seemed strange to me, but apparently it's allowed by code.
Is my math correct?
thanks
steve
#8/3 NMB, 40A breaker.
I did the calculation according to 220.55 Note 1, and the installation seems to be code compliant.
8KW + (20% of 8KW) = 9.6 KW = 40.0A @ 240V
Is this correct?
It seemed strange to me, but apparently it's allowed by code.
Is my math correct?
thanks
steve