gndrod said:
			Bob NH,
Are you saying the 16kw range BC and disconnect can be #8 with a 40a breaker? Please explain the rational of pre-empting [210.19(A)(1)] load being served conductor requrements. Does [220.55] apply to DF calculations only?
The rationale is as follows. Take these IN ORDER.
1.
210.19(A)(1) General says that branch-circuit conductors shall have an ampacity not less than the maximum LOAD to be served.
2.
220.1 explicitly states that Article 220 provides requirements for CALCULATING LOADS, including branch circuit loads.
3.
220.14(B) states that "Load calculations shall be permitted as specified . . .  in 220.55 for electric ranges and other cooking appliances."
4.
220.55 states that the LOAD for ranges and other cooking appliances shall be permitted to be calculated in accordance with Table 220.55.
5.
Note 4 of Table 220.55 states, "Branch-Circuit Load. It shall be permissible to calculate the branch-circuit load for one range in accordance with Table 220.55."
This answers the question about demand factor only. It is permitted to use Table 220.55 for branch-circuit loads and sizing of conductors and OCPD.
6.
Table 220.55, including Note 1, provides the instructions for calculating the demand (LOAD) for ranges from 12 to 27 kW.
The code permits the LOAD to be defined as something less than the nameplate rating.
From Table 220.55; Demand = Load = 8kW + (0.05)(8kW)(Nameplate kW - 12kW)
7. Results of that calculation are:
Nameplate kW = 12; Load = 8 kW; Minimum 40 Amp circuit per 210.19(A)(3)
Nameplate kW = 16; Load = 9.6 kW; Amps = 40
Nameplate kW = 22; Load = 12 kW; Amps = 50
Nameplate kW = 27; Load = 14 kW; Amps = 58.33