gndrod said:
Jon,
"I guess the reality question is, would any contractor make a decision to wire #8 BC to a 16kw range? Would you?"
To add to that reality question.
If the electrician wired a range circuit for a residence, and (IMO...by code) installed a 40 Amp circuit to power that range, who's responsibility is it to insure the circuit is adequate if:
The range has not been selected when the house is rough wired?
The owner (sometime in the future) replaces that range with a larger unit?
As it is...again IMO...the code provides adequate safety by allowing the 40A circuit.
As stated many times on this web site...The code is not a design manual.
8/3NM is rated 50A at 75C, will be connected to a 50A receptacle and protected by a 40A breaker (max.).
Where is the safety concern?
Most likely, the home owner will get tired of nusiance breaker tripping (if it ever trips) and call a electrician or will simply learn what heating elements they can turn on at the same time.
I'm not saying that tripping breakers are a good thing, but will likely become a fact of life as range sizes (KW ratings) increase.
The only solution that I see to this (supposed?) problem is:
Either the code needs to change it's requirements and only allow 60 amp (or larger) circuits for residential ranges ...or...the range manufacturers need to design the range controls to prevent operation of all heating elements at the same time and fix the total at a certain (maximum) KW.
That or some other rule (I don't know what) needs to be established to match range loads to the circuit provided....maybe establish a maximum (range) KW allowed on residential and always wire for the max.
It's beginning to be a bigger problem as the KW rating of 30" residential ranges increase.
There are thousands of residential ranges out there that operate on 40A circuits.
Sooner or later, they will be replaced.
With what?
Most people buy a new range without considering the KW load, or even knowing what it means.
They have the range delivered and "installed" by a delivery man who simply attaches a cord and plugs it in.
Who's problem is it if it trips the existing breaker?
If the circuit is wired to code, it's the homeowners.
If it's not to code, it's the electrician's that wired it.
If we can't read and apply the code as written, what use is it?
Is it fact, or is every part subject to interpretation?
Where is the dividing line?
Just my opinion
steve