JohnJ0906 said:
422.10(A) says (in part) "branch circuits for household cooking appliances shall be permitted to be in accordance with table 220.55"
Johnjo906, Taking that sentence out of 422.10(A) of Part II. Installation leaves a lot of incomplete interpretation to "accordance with Table 220.55".
Let's not overlook the section heading as follows;
NEC 2005 "422.10 Branch-Circuit Rating. This section specifies the ratings of branch circuits capable of carrying appliance current without overheating under the conditions specified."
(When using 220.55, the condition is...an #8 awg Cu conductor, rated for 40A at 60 C [310.16] to a fully lit 16 kW range at a maximum load drawing 67 amps.)
Is this safe? Can you guarantee a client that the circuit conductor terminations will not overheat and last 40 years? Most of all, would you wire your house with this configuration?
Bob NH,
What is the reason why Article 210 was ever written if Table 220.55 is construed for conductor ampacity and sizing for the load being served?
Shame shame. Not once is "the maximum load to be served" mentioned in Table 220.55 and for that matter Article 220. You misquote the NEC.
According to 90.1(C) the NEC is not intended as a design manual for "propositions" of your own wording. At best, save those for cycle 2011.
422.10 Branch-Circuit Rating also states "The rating of an individual branch circuit shall not be less than the marked rating of the appliance or the marked rating of an appliance having combined loads as provided in 422.62."
What is the rating marked NPR of a 16 kW range? Go figure.
Then answer my question to you...Would you wire houses with #8 awg for 16 kW range circuits? BTW use AHJ as a relegating source.
I do not know everything, that is why I have a solid reference base and pay for a membership in the electrical section of the NFPA.
I do not waste my good time and membership fees for a discussion with you.
I challenge you to fork up your own hard-earned bucks for a membership in the NFPA. Read the CYA disclaimer ahead of Article 90 and you can see that everything is all about safety.