gndrod said:
Bob NH,
I feel we are coming together on common ground here. I am glad you realize where the NEC is on safety standpoints in this discussion and why there is a need to make distinctions between 210 and 220.
I am only one of many on this forum who have pointed out the differences in calculation methods for branch circuit conductor ampacity and sizing. Using the Article 220 for calculation of Optional Methods does not allow using Table 220.55. This is the first step to understanding why 210 is needed. Is this in agreement with your interpretations so far?
Article 210 is needed. It says that the conductors shall have an ampacity not less than the maximum load to be served.
Article 220 is also needed, relevant, and not superseded by Article 210. It describes how to calculate the loads for which the conductors must be sized in accordance with the provisions of Article 210.
220 Branch-Circuit, Feeder, and Service Calculations
220.1 Scope. This article provides requirements for calculating branch-circuit, feeder, and service loads.
The concept is quite simple. Article 210 says design the conductors for the loads. Article 220 specifies the permitted methods for calculating the loads.
I repeat below the logic from an earlier post. I have seen nothing to suggest that it is not valid.
The Proposition:
It is permitted to use NEC 2005 Article 220.55 and Table 220.55 for sizing branch circuit conductors and overcurrent protection for individual ranges and for equivalent combinations of cooktops and ovens.
Citations (From 2005 NEC):
422.10(A) Individual Circuits. (Last paragraph) Branch circuits for household cooking appliances shall be permitted to be in accordance with Table 220.55
Article 220 Branch-Circuit, Feeder, and Service Calculations
Part II. Branch Circuit Load Calculations
220.10 General. Branch-circuit loads shall be calculated as shown in 220.12, 220.14, and 220.16.
220.14(B) Electric Dryers and Household Electric Cooking Appliances. Load calculations shall be permitted as specified in . . . 220.55 for electric ranges and other cooking appliances.
220.55 Electric Ranges and Other Cooking Appliances - Dwelling Unit(s). The load for household electric ranges, wall-mounted ovens, counter-mounted cooking units, and other household cooking appliances individually rated in excess of 1 3/4 kW shall be permitted to be calculated in accordance with Table 220.55. . . .
Table 220.55 Demand Factors and Loads for Household Electric Ranges, . . .
Note 4. Branch Circuit Load. It shall be permissible to calculate the branch-circuit load for one range in accordance with Table 220.55. . . .
Conclusion:
Numerous citations in NEC 2005 explicitly support the proposition that the load for an individual range or cooking appliance, and therefore the conductors and overcurrent protection to be determined in accordance with other sections of the code, are permitted to be based on the Demand Factors and Loads of Table 220.55.
Absent any contrary ruling from the NFPA, I believe the proposition stands.