By having more individual units - you still typically increase necessary service or feeder size, but allowable demand factors are not necessarily same ratio so to speak. A single 10 kVA rated unit will have a demand of 100% especially something that isn't capable of varying load level other then on/off. Now put in 100 of them and allowable demand factors exist because they assume that not all of them will be running at same time, they cycle as a thermostat calls for heat/cool, or possibly they even have variable output capability, and not all likely to run at 100%. Said units can potentially run at 100% load at times but are not likely to do so for very long when that does happen.What I find most interesting though is that when you have a MFD with, say, 40 or 60 units, you get to the point where the 220.84 calculation allows you to apply a smaller demand factor, resulting in a smaller distribution panel feeder & smaller service feeder (when compared to the 220.82 calculation)
So in essence, I have to add load (or allow for future load to potentially be added by accounting for it in the panel calculations) in order for the service feeder to be smaller. To me, that's reverse logic.
Also, if you flip this over to the mechanical side of things, the mechanical code doesn't allow you to account for cord & plug space heaters in the calculations for heat loading to determine the appropriate size HVAC unit for a given space. So this is a case, to me, where one hand (electrical) is taking something into account in order to be able to take advantage of the optional calculation, whereas the other hand (mechanical) can't allow that. Though I suppose if you just are making an allowance for it...when I have a unit that has a 100A panel but there's only something like 65-75A on it, adding a dedicated circuit for a 1 kW space heater won't affect that at all
Just seems like a "hole" to me....
So the single 10 kVA unit will need full 10 kVA in the load calculation - but 100 of them that had say an allowable 50% demand factor (totally made up factor here), would still need more VA then the single unit, but only 50 times more instead of 100 times more.