Sorry, what do you mean by "15 minute demand"? I thought that was average power used over a 15 minute interval, so in units of kW it would just be 4 times 15 minute usage in kWh.Our utility will only provide 15 minute usage in kWH and not a 15 minuted demand for residential services.
I think 15min kWH usage should be permitted to be used for demand (multiplied by 4 to get kW, that is), especially for resi. It's unclear to me that there is a robust standard that utilities follow for what constitutes the type of demand data referred to in the code. We've had discussions about the various formats of data before. So I'd appeal to the AHJ's sense of reason.With the smart meters, some utilities will provide the 15 minute demands to make such calculations easy.
Our utility will only provide 15 minute usage in kWH and not a 15 minuted demand for residential services.
I though that was correct, but have been told over and over that it isn't.I thought that was average power used over a 15 minute interval, so in units of kW it would just be 4 times 15 minute usage in kWh.
Lot of people want to use 1 month kWh values to figure out demand, but that is not good enough. Too much swings able to happen in a long average.I though that was correct, but have been told over and over that it isn't.
What would be incorrect about it?I though that was correct, but have been told over and over that it isn't.
no idea, but when I posted to take the 15 minute usage and multiply by 4 to get a 15 minute demand on other sites, I was told that was not correct. When I do the math, I see it is correct, but a number of others told me no.What would be incorrect about it?
As long as you are using the largest 15 minute kWh in the entire period to be analyzed (month, year?), it should be close enough.no idea, but when I posted to take the 15 minute usage and multiply by 4 to get a 15 minute demand on other sites, I was told that was not correct. When I do the math, I see it is correct, but a number of others told me no.
you can download a year of data in a format that works with excel, so you can just sort the usage column from highest to lowest.As long as you are using the largest 15 minute kWh in the entire period to be analyzed (month, year?), it should be close enough.
I always do a MAX function. But that works too. Applying a color gradient can also be useful.you can download a year of data in a format that works with excel, so you can just sort the usage column from highest to lowest.