220V in Wiremold?

Status
Not open for further replies.
Location
Seattle
Occupation
Electrical Wholesale/Industrial
Hello all.

I am trying to get a heater circuit moved from (stupid) ceiling heat to a standard baseboard.

GC is telling me the electrical code prohibits running 220V in Wiremold.

Seems either wrong or excessively cautious.

From what I’ve seen in buildings almost everywhere, Wiremold is even used for 277V lighting circuits.

Jurisdiction is City of Seattle.

thanks!
 
You are correct and unless Seattle has an amendment to the NEC the GC is wrong
 
BTW, we have members as well as a moderator from the Seattle area, I'm sure they will let us know if there is a local code.
 