220V in Wiremold?

Location
Seattle
Occupation
Electrical Wholesale/Industrial
Hello all.

I am trying to get a heater circuit moved from (stupid) ceiling heat to a standard baseboard.

GC is telling me the electrical code prohibits running 220V in Wiremold.

Seems either wrong or excessively cautious.

From what I’ve seen in buildings almost everywhere, Wiremold is even used for 277V lighting circuits.

Jurisdiction is City of Seattle.

thanks!
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
You are correct and unless Seattle has an amendment to the NEC the GC is wrong
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
BTW, we have members as well as a moderator from the Seattle area, I'm sure they will let us know if there is a local code.
 