I have recently learned that Rio Power Co sets subject aerial transformers to serve just about houses, strip malls, etc. I believe the subject voltage is comparable to NEC 208Y/120V.
Appreciate your help on this 2 part design:
First I have a group of buildings with a total load of 35kva and maybe up to 50kva all single phase. Rio will set the pole and install 3 phase TX and run their secondary to a meter below the TX. I will come out of their meter and take 4 secondary wires about 100 feet to a main building. I think I should install a 3 phase 200 amp panel, even though I do not need 3 phase. Then I suppose I use all of those 3 phases for single phase load balancing service throughout the main building, and to feed other building's panels that are downstream. This way I will have single phase at 220v AB, BC, and AC. And also 127v A, B and C phases to neutral, with the neutral grounded. Is this approach ok?
What type of panel do I use for this?
Part 2: I must serve 5 homes UG each will have a 100 amp panel. Rio does not use padmounts so they will set another 3 phase TX pole and come down the pole to their meter. Then I go from the meter onto a rack mounted trough, then split-bolt the 4 wires in the trough(abn, bcn, acn, abn and bcn)and go out of the bottom of the trough to 5-100 amp fused disconnect switches. Then out of the bottom of the switches UG to each of the homes 100 amp panels. Is this approach ok? Thank you.
[ July 29, 2004, 09:16 PM: Message edited by: pelican ]
Appreciate your help on this 2 part design:
First I have a group of buildings with a total load of 35kva and maybe up to 50kva all single phase. Rio will set the pole and install 3 phase TX and run their secondary to a meter below the TX. I will come out of their meter and take 4 secondary wires about 100 feet to a main building. I think I should install a 3 phase 200 amp panel, even though I do not need 3 phase. Then I suppose I use all of those 3 phases for single phase load balancing service throughout the main building, and to feed other building's panels that are downstream. This way I will have single phase at 220v AB, BC, and AC. And also 127v A, B and C phases to neutral, with the neutral grounded. Is this approach ok?
What type of panel do I use for this?
Part 2: I must serve 5 homes UG each will have a 100 amp panel. Rio does not use padmounts so they will set another 3 phase TX pole and come down the pole to their meter. Then I go from the meter onto a rack mounted trough, then split-bolt the 4 wires in the trough(abn, bcn, acn, abn and bcn)and go out of the bottom of the trough to 5-100 amp fused disconnect switches. Then out of the bottom of the switches UG to each of the homes 100 amp panels. Is this approach ok? Thank you.