am looking for opinions on 225.30 We are working on a townhome. Load calculations push it over 200A.
I am looking for some input from some individuals that are smarter than me.
There is a detached garage where the main service is built (Overhead utilities come from the alley). Our engineer designed the service (It must be reviewed and approved by the city - Denver) to be a 300A overhead service. We used a Siemens meter combo (#MK0402L1400SC) with a150A and a 200A Main breaker.
We ran feeds to two panels on the residence (W/Main Breakers). The 150A feed passes through a feed through lug panel (Panel G - Garage) before it goes underground to the residence.
This panel is used for the garage circuits (Lights, 20A receptacle circuit and EV charger). We are being told that this design violates 225.30 (B). We are being told that by doing this the feeder does not originate in the metering equipment.
We suggested that we bring a feeder circuit back from the main residence to Panel G, but were told this too is a violation.
We are getting no feedback from the city. We suggested that since they are the AHJ 225.30 (C) (2) could apply.
Thank You!
am looking for opinions on 225.30 We are working on a townhome. Load calculations push it over 200A.
I am looking for some input from some individuals that are smarter than me.
There is a detached garage where the main service is built (Overhead utilities come from the alley). Our engineer designed the service (It must be reviewed and approved by the city - Denver) to be a 300A overhead service. We used a Siemens meter combo (#MK0402L1400SC) with a150A and a 200A Main breaker.
We ran feeds to two panels on the residence (W/Main Breakers). The 150A feed passes through a feed through lug panel (Panel G - Garage) before it goes underground to the residence.
This panel is used for the garage circuits (Lights, 20A receptacle circuit and EV charger). We are being told that this design violates 225.30 (B). We are being told that by doing this the feeder does not originate in the metering equipment.
We suggested that we bring a feeder circuit back from the main residence to Panel G, but were told this too is a violation.
We are getting no feedback from the city. We suggested that since they are the AHJ 225.30 (C) (2) could apply.
Thank You!