Jim W in Tampa said:Why not,they require afci breakers and none that do whats required have been made yet
"They" do not live in NJ...we are ahead of the curve, the other 49 can be the "control" for the AFCI experiment...AFCI's are optional here
Jim W in Tampa said:Why not,they require afci breakers and none that do whats required have been made yet
My guess is because the feeder disconnecting means is in a seperate (possibly inacessable) building... remember they are treating this as main service disconnect for the detached building.Jim W in Tampa said:Either 2 pole or a 60 amp pull out.Why is a receptacle or switch ok as disconnect for garbage disposal but not here ?Its the same switch.
celtic said:"They" do not live in NJ...we are ahead of the curve, the other 49 can be the "control" for the AFCI experiment...AFCI's are optional here![]()
Jim W in Tampa said:Isn't that sorta a time bomb ? If someone dies and its proven an afci would have saved them how will they defend this in court ?
Quite possible, yes.Jim W in Tampa said:Isn't that sorta a time bomb ?
That's a good question...and people HAVE died in Flanders, NJ:Jim W in Tampa said:If someone dies and its proven an afci would have saved them how will they defend this in court ? Its a willfull endangerment of the public.
As I recall, there was recall of AFCIs... (http://www.cpsc.gov/cpscpub/prerel/prhtml05/05035c.html)Jim W in Tampa said:Why exactly did they remove them ?
...but not always:Jim W in Tampa said:They work fine in the other 49.
DaveTap said:(Is a multi-wire branch circuit counted as one or 2 circuits here?)
So if you have a detached garage and want to run a 15 amp lighting circuit and say a 20 amp for a GFCI you need a 30 amp disconnect? I'll stick to my standard installation of a 100amp MBR panel in the garage... then run outdoor lighting circuit on 15amp 3-way back to house. Its only a few bucks more anyway and the customer can plug in his welder and compressor no problem.![]()
I'm feeling a little slow tonight.iwire said:Yes, 225.33(B) requires that.allenwayne said:Originally Posted by allenwayne
George wouldn`t you need some type of handle tie to break both conductors on a MWBC if toggle switches are used ?
Wouldn't two single pole switches without handle ties disconnect all ungrounded conductors with less than six throws of the hand?225.33(B) Single-Pole Units. Two or three single-pole switches or breakers capable of individual operation shall be permitted on multiwire circuits, one pole for each ungrounded conductor, as one multipole disconnect, provided they are equipped with handle ties or a master handle to disconnect all ungrounded conductors with no more than six operations of the hand.
I can?t find a section that will allow a multi pole switch for the disconnecting means.stickboy1375 said:I think I will just start installing a 2 pole switch for my disconnect....
georgestolz said:A handle tie is required by 210.4 and 210.7 if two legs of a MWBC or two seperate circuits terminate on a single device.
georgestolz said:
A MWBC may supply seperate receptacles without handle ties.
I just woke up, so I'm still feeling slow.
jwelectric said:225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.
All I see in the exception is single pole, three way and four way switches.