Sberry
- Brethren, MI
- farmer electrician
I did one similar to post 11 a while back,, 20A from the main building to the second thru a single pole switch and then to the 3rd which had a single pole switch.
A 60-amp main breaker in the secondary panel would serve no purpose…
Said language in 225.39 also gives the lie to the interpretation that "the feeder or branch-circuit disconnecting means" refers to the supply end overcurrent device, as that would have to be a single OCPD.Note that 225.39 says that where the disconneting means is more than one breaker or switch, you can combine the ratings of all the switches/breakers to calculate the rating of the disconnecting means. If you have 5 breakers, and all are 15A, that is a 75A disconnect which is large enough. No 60A breaker should be needed.
Or 45a (and 30a) if you have 120/240v.If you have 5 breakers, and all are 15A, that is a 75A disconnect which is large enough.
I just wonder what the thinking was of the person who installed/wired the secondary panel with only a 30-amp feeder to a panel that could very likely pull over 40-amp if really used to it's fullest extent.
Incorrect See 230.41(B).Since there is no history of a minimum service switch rating to size service conductors, I dont think they ever intended to make a code policy change in 1999, rather the intent was to just copy the wording to Article 225 where it made more sense to be located.
This section isn't clear on how to handle a multi pole breaker. Does a double pole 20A count as 20 or 40 amps for the disconnect rating? Since it could be all single poles summing 6 x 15A at 90A, I can see a good argument that 6 x 15A double poles is 180A. But is says "combine the ratings" and I would say a 20A breaker is rated at 20A whether it is 1 pole, 2 pole, or 3 pole.Or 45a (and 30a) if you have 120/240v.
20a.Does a double pole 20A count as 20 or 40 amps for the disconnect rating?
I see six 1p 15a breakers as 45a, three on each line. Six 2p 15a breakers would be 90a.Since it could be all single poles summing 6 x 15A at 90A, I can see a good argument that 6 x 15A double poles is 180A.
230.42(B) in my 2023 book thank you.The typos are killing me. 230.41(B)???
The lack of any comparable language in 225 is yet another sign that the 225.39 minimums apply to the size of the disconnecting means at the building supplied, not the overcurrent device at the supply end of the branch circuit or feeder. Instead we have 225.5, which says to size the conductors based on the load calculation.230.42(B) in my 2023 book thank you.