We had a recent thread about this for services but now I am faced with the following:
There is a pump house has more than two circuits on a 4 wire 10/3 UF cable.
I have not done a load calc but I imagine its under 7200W.
The panel has rusted out and needs replaced.
There is a 2 pole 30 in the main house for this feeder, that is the feeder disconnect.
Now I don't want to replace this feeder.
Can I add a 60A disconnect on the main house where the LB is now and the conduit dives into the ground ? ?
Or would the 30A breaker in the service still be the feeder disconnect?
And if so can it be a 60A breaker or does it need to be a 60 amp rated fused disconnect with 30A fuses to create a new feeder?