Wyane I appreciate the help, I really do.
But this CMP stuff while not new to me, I have not payed close attention to it.
I know if they like part of a proposal they can 'accept in part'. I am told 2002 was the cycle after this was added, my boss has a 1996 book and its not in there.
So the question comes up and got knocked down and people notice. Why ask again when you know the answer?
That code change proposal was for over-current protection nothing to do with the "branch circuit or feeder disconnect".
Per the definition of a feeder there needs to be a disconnect at the beginning of the feeder.
Where else is a "branch circuit or feeder disconnect" ?
This fella is a long time inspector and clearly stated his argument.
If a "branch circuit or feeder disconnect" is not different from a "building or structure disconnect" and "the disconnecting means specified in 225.31" why word it differently just that one time in 225.39?
Why not say like they did in 225.36 "The disconnecting means specified in 225.31" ?
But this CMP stuff while not new to me, I have not payed close attention to it.
I know if they like part of a proposal they can 'accept in part'. I am told 2002 was the cycle after this was added, my boss has a 1996 book and its not in there.
So the question comes up and got knocked down and people notice. Why ask again when you know the answer?
That code change proposal was for over-current protection nothing to do with the "branch circuit or feeder disconnect".
Per the definition of a feeder there needs to be a disconnect at the beginning of the feeder.
Where else is a "branch circuit or feeder disconnect" ?
This fella is a long time inspector and clearly stated his argument.
If a "branch circuit or feeder disconnect" is not different from a "building or structure disconnect" and "the disconnecting means specified in 225.31" why word it differently just that one time in 225.39?
Why not say like they did in 225.36 "The disconnecting means specified in 225.31" ?