225 KVA Isolation Transformer

Status
Not open for further replies.

Purr24

Member
Location
Pennsylvania
Occupation
Electrician
I am installing an Isolation Transformer Prime 480v and Sec. 480v for a CT Scan room. I have a fused disconnect on secondary side of transformer first means of disconnect are my Neutrals and Grounds bonded together at this switch
 
I am installing an Isolation Transformer Prime 480v and Sec. 480v for a CT Scan room. I have a fused disconnect on secondary side of transformer first means of disconnect are my Neutrals and Grounds bonded together at this switch
If the secondary is a wye system then you would need a system bonding jumper on the secondary side. It could be at the disconnect. I think it might need to be a service rated switch.

You would also need a grounding electrode system and a grounding electrode conductor connected to this same point.

There would be no connection of the neutral between the primary and secondary side, except via the EGC.
 
#3 switched removed 175 amp breaker in A1 switch
d4559ef0e814f137961251cda0cbc128.jpg


Sent from my Pixel 2 XL using Tapatalk
 
Your print shows neutrals and grounds bonded at the transformer.

As @petersonra notes, you must have a neutral/ground bond _somewhere_, and it could be at the disconnect. But it is equally valid to have it at the transformer. There should be only _one_ neutral/ground bond.

-Jon
 
This is an isolated grounded system, and while we can debate the usefulness of such a system, the system bonding jumper needs to be at the transformer to accomplish what the engineer thinks an isolated grounding system can do.
 
I think the way to go is bond Netral and ground in A-1 Disconnect with bonding screw. Isolated ground and equipment ground all bonded together in the Transformer. So much for isolation.
 
Isolated ground and equipment ground all bonded together in the Transformer. So much for isolation.
But that is how an isolated ground system should be installed. A single ground point is the intent not actual isolation, each grounding conductor/path is isolated from all other conductors/paths except at one common point.
 
Last edited: