tryinghard said: Post #4
Thanks all, interesting thing is the residential 320 doesn’t use CTs nor does the 2-200 the load routes through the meter. The calc might have a mistake but not likely way off, the customer wants the meter main remote at the property line about 300’ from the house, and we’d like to pull one feeder rather than two. The calc method used is Art 220 and Annex D2.a example method, this is a large house: 3,570 sq ft, 2 kitchens (with ranges, dish/garbs, built in micros), 2 laundry’s & dryers, 2 ACs (4.5 ton & 1 ton), 1 vehicle charger (5.4kva), 1 extra freezer, I come up with 25.044 Kva general load and 49.787 kva