I don't think the issues will be resolved by the 9/1/26 expiration date, but the first draft of the 2026 code says.
Effective September 1, 2026, GFCI or SPGFCI protection shall be provided for listed HVAC equipment.
While the SPGFCI may solve the problem, they are not readily available as as far as I know there are no plans to have a breaker type SPGFCI. They are all large, and expensive stand alone devices, and they require an additional conductor between the SPGFCI device and the protected load. This is used to verify that the EGC is intact. If either the EGC or the "ground check" conductor is open, the device will open the power circuit.