230.2 conductor
hhsting
Glen bunie, md, us
Junior plan reviewer
The first paragraph of NEC 2014 section 230.2 says:
“For the purpose of 230.40 exception no. 2 only underground sets of conductors, 1/0awg and larger, running to the same location and connected together at their supply end but not connected together at their load end shall be considered to be supplying one service”
Question: What are the underground sets of conductors 230.2 first paragraph referring to? Service lateral, service entrance conductor or both or some other conductors. It just says conductors
As reference NEC 2014 section 230.2 first paragraph mentions 230.40 exception no.2 which is NEC 2014 version:
“Where two to six service disconnecting means in separate enclosure are grouped at one location and supply separate loads from one service drop, set of overhead service conductors, sets of underground service conductors, or service lateral, one set of service entrance conductors shall be permitted to supply each or several such equipment enclosures”