Attached sketch shows two tenants A and B. The electrical room which is accessible from outside houses SWBD1 and SWBD2. SWBD1 is new with main service disconnect of 800A and so is the service conductor underground from utility transformer to SWBD1. SWBD 2 is existing with 600A main service disconnect and underground service conductor is existing from utility transformer to SWBD2.
SWBD2 all feeder breakers serve Tenant B space. SWBD1 one feeder breaker serves panels A1, B1 and XFMR A in Vacant Tenant A space and all the rest feeder breaker serve Tenant B space. In future of course when Tenant A is not vacant it will have its one electric service so SWBD2 all feeder breakers would serve Tenant B space only.
Incoming service consorts to SWBD2 is 1 set of 500 kcmil AL and SWBD1 is 2 sets of 500kcmil(AL) both are verified by utility to be sufficient ampacity.
I am wondering if the new SWBD1 underground service would be allow to be considered one service in building since SWBD1 and SWBD2 service disconnects are grouped in one location and supply come from one source in underground service conductors each greater then 1/0AWG first paragraph 230.2. However I am confused by first paragraph of 230.2 which points to 230.40 exception no. 2 which has language supply separate loads and is confusing in my case.
Questions:
1. Would 230.2 first paragraph allow new additional SWBD1 service conductors and can be considered one service overall in future when Tenant A is removed and both SWBD1 and SWBD2 serve Tenant B space only or this is considered multiple services?
2. What about present situation where SWBD1 serves TenantA and Tenant B while SWBD2 serve Tenant B space only in regards to would 230.2 first paragraph allow new additional SWBD1 service conductor to be considered one service or this would be considered two separate services?
Please note this thread is about multiple services not about tenants access to readily accessible overcurrent protection
SWBD2 all feeder breakers serve Tenant B space. SWBD1 one feeder breaker serves panels A1, B1 and XFMR A in Vacant Tenant A space and all the rest feeder breaker serve Tenant B space. In future of course when Tenant A is not vacant it will have its one electric service so SWBD2 all feeder breakers would serve Tenant B space only.
Incoming service consorts to SWBD2 is 1 set of 500 kcmil AL and SWBD1 is 2 sets of 500kcmil(AL) both are verified by utility to be sufficient ampacity.
I am wondering if the new SWBD1 underground service would be allow to be considered one service in building since SWBD1 and SWBD2 service disconnects are grouped in one location and supply come from one source in underground service conductors each greater then 1/0AWG first paragraph 230.2. However I am confused by first paragraph of 230.2 which points to 230.40 exception no. 2 which has language supply separate loads and is confusing in my case.
Questions:
1. Would 230.2 first paragraph allow new additional SWBD1 service conductors and can be considered one service overall in future when Tenant A is removed and both SWBD1 and SWBD2 serve Tenant B space only or this is considered multiple services?
2. What about present situation where SWBD1 serves TenantA and Tenant B while SWBD2 serve Tenant B space only in regards to would 230.2 first paragraph allow new additional SWBD1 service conductor to be considered one service or this would be considered two separate services?
Please note this thread is about multiple services not about tenants access to readily accessible overcurrent protection