texie
- Fort Collins, Colorado
- Electrician, Contractor, Inspector
Per 230.43 (15) and you are using LFMC between, say, a meter socket and a service disconnect you need to install a SSBJ. But if you have a meter socket with a bonding jumper (most would have a permanent bond anyway) and you have the neutral bonded at the service disconnect this would comply with 250.92 and that is all you need for a fault return path. What purpose does the SSBJ serve?
After all, if you used, say PVC, no bonding SSBJ would be required. I realize that LFMC is metallic and can't carry the fault current but how would a SSBJ help if you already comply with 250.92 by bonding to the neutral at each end?