Re: 230.54
I have seen an instance where water went into a rectangular meter socker through the upper cable and dripped right down into the lower cable. That means that a factory installed drain hole does not necessarily provide any protection.
The requirement for a piped drain only applies in 3 situations. The first one is the very rare service where a weatherhead is outside of an explosionproof area and some of the service equipment needs to be explosionproof. The second situation where service equipment needs to be dust-ignitionproof would apply to farms, bakeries, and grain elevators. The 3rd situation is a bushing type supply riser such as for over 600 volt services where the service is more elaborate anyways.
Since a transformer vault is usually required to have a reliable floor drain anyways, the requirement for a piped drain is not a hardship. Rather, the likelyhood of a bushing type supply riser admitting water is a bit higher and the requirement is just there to require something more professional than water dripping out the bottom of a pull box.
[ April 16, 2005, 02:27 AM: Message edited by: mc5w ]
I have seen an instance where water went into a rectangular meter socker through the upper cable and dripped right down into the lower cable. That means that a factory installed drain hole does not necessarily provide any protection.
The requirement for a piped drain only applies in 3 situations. The first one is the very rare service where a weatherhead is outside of an explosionproof area and some of the service equipment needs to be explosionproof. The second situation where service equipment needs to be dust-ignitionproof would apply to farms, bakeries, and grain elevators. The 3rd situation is a bushing type supply riser such as for over 600 volt services where the service is more elaborate anyways.
Since a transformer vault is usually required to have a reliable floor drain anyways, the requirement for a piped drain is not a hardship. Rather, the likelyhood of a bushing type supply riser admitting water is a bit higher and the requirement is just there to require something more professional than water dripping out the bottom of a pull box.
[ April 16, 2005, 02:27 AM: Message edited by: mc5w ]