sceepe
Senior Member
Got a large commercial service (1600 amps) about 80% complete. AHJ has just decided that length of service entrance conductors is too long and wants an enormous exterior disconnect. Funny thing is, he had no problem with it during plan review. Reading 230.70 commentary, it doesn't look like I have many options. One that I was considering is getting the poco to install disconnect on the pad mount. Much smaller disconnect on the high voltage side. Even if we had to buy the disconnect, it may be cheaper than the secondary side disconnect. Has anybody ever seen a POCO do this?