jwelectric said:
dnem said:
408.34(A) says that lighting and appliance panels are ones with more than 10% of their breakers on circuits of [408.34] 30 amps or less. The note between subitem A and subitem B of item 20 says *See Item 23 for lighting and appliance panelboards. which seems to be saying that the other items [20, 21, 22, & 24] are not applicable to lighting and appliance panels. Is that correct ?
408.36(A) states that a lighting and appliance panelboard must be protected by not more than two mains.
In your panel as outlined above you have one thirty amp breaker which would constitute 1.2% of the Overcurrent devices in that panel.
Hang on a minute, you?ve already lost me.
200, 200, 100, 60, 40, & 30 that?s 6 twopole breakers. The 30 would be 1/6th of the total number of breakers or 16% of the breakers.
?one thirty amp breaker which would constitute 1.2% of the Overcurrent devices in that panel?
I don?t understand what you?re saying.
jwelectric said:
408.36(A) states that a lighting and appliance panelboard must be protected by not more than two mains.
In your panel as outlined above you have one thirty amp breaker which would constitute 1.2% of the Overcurrent devices in that panel.
If this 30 amp breaker supplies a circuit that also utilizes the neutral then this is a lighting and appliance panel and would require a main.
Are you saying this because the 30amp is 16% which is over the 10% requirement ?
Are you saying that it can have only one main or a max of
two mains [408.36(A)] ?
And where does 408.36(A)x2 come into play ?
jwelectric said:
The key words found in rule 20 of UL?s marking guide is ?A panelboard with the neutral insulated from the enclosure?
When using this type panel then all spaces must comply to the six disconnect rule. This panel has the neutral insulated from the enclosure and is not the main.
?When using this type panel then all spaces must comply to the six disconnect rule.?
What do you mean by that ? ?must comply? ?
If the neutral is
not factory insulated from the enclosure, there is a 6 disc max.
If the neutral
is factory insulated from the enclosure, if a main bonding jumper is installed to use the panel as a main, there is a 6 disc max.
There?s no difference according to 230.71.
We apparently are talking about to different concepts but I can?t figure out what you?re saying.
?This panel has the neutral insulated from the enclosure and is not the main?
And then I
add a main bonding jumper and then it
is a main.
jwelectric said:
dnem said:
Does subitem A of item 20 refer to the same thing that jim dungar was referring to ?
jim dungar said:
Question 3: Yes There are many situations where more "breaker space" than normal is required for to accomodate 6 disconnects in a panel (i.e. shunt trip breakers often take more space, plug-on TVSS units, and finally actual breakers feeding TVSS and power monitoring)
If this is the kind of thing that's referred to in subitem A of item 20 then would it be correct to say that 42 slot MLO panels could not be used as a main regardless of the number of disconnects originally installed ?
No, back up and read lines 18 and 19 to see what makes a panel
Suitable for Use as Service Equipment.
Line 20 is only addressing a panel that has the neutral that is isolated from the enclosure.
So what does this sentence mean:
There must be at least one combination of switching units that can be mounted to occupy all available space for switching units.
David