If a service switchboard has no main breaker, has 6 breakers that supply loads, and has one provisioned space for a possible future breaker, does this violate the cited article? To be specific, I am asking whether the provisioned space counts the same as it would if there were a breaker installed?
My answer is yes, this is a violation. I am seeing this installation in the plans for a remodel project that I am reviewing. I want to get a few other opinions before I write this up as a design review comment.