There's a slight hole in the definition of "service conductors."
230.91 specifies that the "service overcurrent device" shall be integral to the "service disconnecting means" or located "immediately adjacent thereto." And the definition of "service equipment" covers both switches and circuit breakers at the service.
However, the definition of "service conductors" specifies "The conductors from the service point to the service disconnecting means." So when the service overcurrent device is not integral to the service disconnecting means, we have conductors from the service disconnecting means to the service overcurrent device, and they are not not technically service conductors.
It's unclear if those conductors are "feeders", as that definition refers to circuit conductors between "service equipment" and the branch circuit OCPD. So if you take that to mean downstream (away from the utility) of all the service equipment, feeders would only start on the load side of the service overcurrent device.
However, they are arguably "service entrance conductors," as that definition does not refer to the "service disconnecting means" but rather to "service equipment."
Anyway, this is clearly a flaw in the definition of "service conductors," which should read "The conductors from the service point to the service equipment."
Cheers, Wayne