I think I agree with Elect117.What about the scenario that I alluded to earlier. On, say, a 400A service you put a SUSE fused disconnect with 600A fuses, followed by an "immediately adjacent" SUSE 400A enclosed circuit breaker as the service overcurrent device.
Not sure why you'd do that, maybe the 400A fuses are out of stock or would cause some other problem.
In this case I'd say that unless the first disconnect qualifies as an 'Emergency Disconnect' or 'Meter Disconnect' or some such, then you don't get out of calling it the service disconnect. So your service conductors would have to be protected by the 600A fuses.