As would the NEC itself.
True. The nec doesn't highlight everything that is objectional, and what is objectional to one inspector might not be to the next. But I agree with you, I am just looking at reasons why one might not agree that 250.85(3) allows 3 wire after the emergency disconnect, with objectionable current being one reason. Now there would be another enclosure on the line side of the service disconnect bonded to neutral.
 
True. The nec doesn't highlight everything that is objectional, and what is objectional to one inspector might not be to the next. But I agree with you, I am just looking at reasons why one might not agree that 250.85(3) allows 3 wire after the emergency disconnect, with objectionable current being one reason. Now there would be another enclosure on the line side of the service disconnect bonded to neutral.
Edit 230.85(3). It's early
As would the NEC itself.

Edit 230.85(3). It's early
 