- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
The installer asked my co-worker for the settings of a service breaker?s ground fault trip. This is a concept that I do not fully grasp. 230.95 requires this protection in certain systems, and 230.95(A) gives the maximum settings. My questions are,
1. Exactly what type of failure would cause this device to trip? What I am looking for is the current flow path.
2. Why is it acceptable to allow almost 1200 amps to flow along that path without initiating a trip, and why is it acceptable for as much as 3000 amps to flow for an entire second, before initiating a trip?
1. Exactly what type of failure would cause this device to trip? What I am looking for is the current flow path.
2. Why is it acceptable to allow almost 1200 amps to flow along that path without initiating a trip, and why is it acceptable for as much as 3000 amps to flow for an entire second, before initiating a trip?