Our resistively grounded system is sized to limit the neutral current to 5 amps (approx 69 ohms for 600V and 55 ohms for 480V). There is literally a resistor in series with the neutral. If you tried to supply a line-to-neutral load you would create a voltage divider. Simply put, stuff wouldn't work.Originally posted by lizzie14:
We do have a 480/277V WYE secondary on our transformer. I saw where the code said you could not serve line-to-neutral loads. Why is this if the voltage is 277V from Line-to-Neutral.
All impedance grounded systems I have seen have the resistor between the neutral and the ground. So any load connected between neutral and line would get 277V and would work fine. But, the code clearly says, "No line to neutral loads".Originally posted by tepres:
There is literally a resistor in series with the neutral. If you tried to supply a line-to-neutral load you would create a voltage divider. Simply put, stuff wouldn't work.