That is a conditional thing though. If you have metal raceways, lot of structural steel, lots of metallic piping, etc. you may have a nearly zero ohm return path through those objects. If you have wood framed building, non metallic piping systems and only real path back to the grounded service conductor is via wire type EGC's you often will have higher ohm path through that EGC than you will if you have a fault from an ungrounded conductor to the grounded conductor (grounded phase) because the EGC likely is smaller than the grounded conductor.I'm only speaking of the fault circuit path itself, not the dynamics of the source. Two wires of equal length versus one wire and basically a zero ohm conductor. The ground fault circuit is almost half the impedance of the line to line short, everything else being equal.
A fault between a grounded conductor (with no incidental parallel paths) and an ungrounded conductor will have same fault current as if you had a fault between the two ungrounded conductors the same distance away from the source.
With a true neutral conductor as the grounded conductor you will have less ohms in a line to ground fault because you are only passing through half the source windings as you would with a line to line fault. But this only ends up applying at short conductor lengths from the source as resistance of the conductor along with the lower voltage to neutral than to another phase eventually works out to leaving you with higher available fault current on line to line faults as you get far enough away from the source.
But we were recently talking corner ground delta - it is a very balanced system if full delta and of all same size coils, it just happens to have one point that is grounded but other than that is still equal potential and equal impedance from each corner to any other corner of the source itself.