230 VAC 3 Phase???

Status
Not open for further replies.

ephesus

Member
Location
NY
Thanks in advance!

I am designing a panel with customer specified 230V 3 Phase Input.

What kind of power is this? Is it really 240V with a neutral and a high leg?

Or are we talking about 208Y that is 208 leg to leg and 120 leg to neutral.

Thanks,

E
 
What is available from your POCO in the area? That may be a limiting factor. Many customers do not know what they need. What kind of occupancy will it be?

Our rural customers may have 240 with a hi leg as you described. Both 208 Wye and 240 hi leg Delta may be available in the bigger towns. Corner grounded Delta is getting more rare all the time but existing irrigation installations may still have it.
 
It's customer supplied 230 VAC. It's for a water treatment plant, so I am leaning toward 240 VAC.

Why do we use 230 VAC for 240 VAC systems?

460 vs 480
115 vs 120 etc.

Thanks

E
 
Ok thanks guys... using your chart we should be able to get the 230 VAC with 240 VAC leg to leg.

Thank you,

E
 
Technically, you will GET 240V leg to leg. The EQUIPMENT is designed for 230V on purpose, so that the voltage drop from the service to the motor doesn’t negatively affect the motor performance and life. That’s what that chart was telling you; 230V is the UTILIZATION voltage, 240V is the DISTRIBUTION voltage. That is the normal way of the world. You’re good to go.
 
Technically, you will GET 240V leg to leg. The EQUIPMENT is designed for 230V on purpose, so that the voltage drop from the service to the motor doesn’t negatively affect the motor performance and life. That’s what that chart was telling you; 230V is the UTILIZATION voltage, 240V is the DISTRIBUTION voltage. That is the normal way of the world. You’re good to go.

I’ve had to explain this to far too many people who should already know it.
 
I think the reason for 230 vs 240 has been explained well enough.

That said you apparently have a 240 volt "nominal" system, but without other details you do not know if it is high leg delta, corner grounded delta, or even possibly an ungrounded system, all of which could possibly impact what you may put into your panel.
 
I’ve had to explain this to far too many people who should already know it.

Same here. But honestly, I was in the industry for probably a decade before I had it explained to me. I kind of blindly accepted the subtle differences in voltage numbers based on my original J-man telling me “It’s no big deal, don’t over think it and move on.” I did that until I just couldn’t accept it any more and dug into it a little. Later when I went back to school for an Engineering degree, they never mentioned it, not once. So I chose it as a topic for an oral presentation, complete with background research etc. The prof said he had never heard the full story. Go figure...
 
Well....actually the utility will set substation regulators or LTC's at 120/240V +/_ 5%. That means it could be as high as 126/252V on the high side. We try to keep the voltage close to the upper limit at the substation in order to keep the voltage higher at the end of long circuits. Sometimes keeps from having to install line regulators or capacitor banks.
 
Well....actually the utility will set substation regulators or LTC's at 120/240V +/_ 5%. That means it could be as high as 126/252V on the high side. We try to keep the voltage close to the upper limit at the substation in order to keep the voltage higher at the end of long circuits. Sometimes keeps from having to install line regulators or capacitor banks.

Hate regs and cap banks :rant: - yes I can understand wanting to avoid them!
 
Well....actually the utility will set substation regulators or LTC's at 120/240V +/_ 5%. That means it could be as high as 126/252V on the high side. We try to keep the voltage close to the upper limit at the substation in order to keep the voltage higher at the end of long circuits. Sometimes keeps from having to install line regulators or capacitor banks.

Yes, that chart I posted reflects that. Same numbers. Tolerances/parameters.
 
One other thought....kinda still on the subject. I'm old enough to have heard about 110/220, 115/230 and finally 120/240. Was it ever really 110/220? If so was it raised to allow for smaller wire to get the same watts? Just curious.....are we headed to 130/260? Or maybe 220 like Europe? Inquiring minds like mine want to know!:huh:
 
One other thought....kinda still on the subject. I'm old enough to have heard about 110/220, 115/230 and finally 120/240. Was it ever really 110/220? If so was it raised to allow for smaller wire to get the same watts? Just curious.....are we headed to 130/260? Or maybe 220 like Europe? Inquiring minds like mine want to know!:huh:

Europe is now 230/400Y. Used to be 220/380 and the UK 240/415- but then came "harmonization" In a lot of places, especially the UK, its still that way (240 instead of 230).
 
I do believe motors and such use those voltages. NEMA thing.

Water treatment plant - motors/pumps- 230VAC speced.

Need to know if 208V is acceptable. Otherwise Delta will be needed for 240V.

It's been my experience that unless a motor has a nameplate rating of 208-230 (some do, but may require different wiring connections), a 230V motor will not work well (or at all) on 208. 230 on 240 is fine, 460 on 480 is fine.

Most of my motor experience has been with larger 3 phase, though.
 
Same here. But honestly, I was in the industry for probably a decade before I had it explained to me. I kind of blindly accepted the subtle differences in voltage numbers based on my original J-man telling me “It’s no big deal, don’t over think it and move on.” I did that until I just couldn’t accept it any more and dug into it a little. Later when I went back to school for an Engineering degree, they never mentioned it, not once. So I chose it as a topic for an oral presentation, complete with background research etc. The prof said he had never heard the full story. Go figure...

I always respected my professors who were willing to learn - far too rare IMO. And you’re right, this concept is not taught formally in Engineering schools.
 