It's what he didn't say that I'm addressing. "The elements failed in a rupture type manor (split down the length) Said unit is built with this from the factory but seems a little odd to me."
This leads me to believe that the 230v heater failed and that there was 480v applied across the failure which resulted in the failure ending up to be a failure in a rupture type manor.
I you had one 230v heater fail where the element opened you will have 480v across that failure and not 230v which would result in significant more damage.
That is understandable at the initial installation, but OP says they have been replaced more than once, is it safe to assume there may be design issues? Simple oil level switch would help with preventing from running dry. I did suggest earlier that if these indeed a water heater element by design that maybe they would not perform as well for heating oil, nobody has replied with any thoughts on that.