I'm looking at a job that I need some input on. A restaurant owner bought a used walk in cooler. The nameplate ratings are as follows:
Compressor: 230V, RLA 6.4A, LRA 34.0
Fan motor: 230V, FLA 1.3A
Evaporator: 115V 2.3A
My question is can I just pull 4 conductors (H-H-N-G) and use one leg of the 230V feed for the evap or am I required to pull a separate circuit? One of the issues is that he has one panel that has 2 spaces left in it and one panel that has one space left so if I needed separate circuits I would need to pull from 2 separate panels (though they are next to each other).
Any thoughts/ input would be appreciated.
Compressor: 230V, RLA 6.4A, LRA 34.0
Fan motor: 230V, FLA 1.3A
Evaporator: 115V 2.3A
My question is can I just pull 4 conductors (H-H-N-G) and use one leg of the 230V feed for the evap or am I required to pull a separate circuit? One of the issues is that he has one panel that has 2 spaces left in it and one panel that has one space left so if I needed separate circuits I would need to pull from 2 separate panels (though they are next to each other).