Had a situation the other day where a new A/C unit was installed that required 240V power. The only source that we had avaliable was a 230V L-G transformer (European Equipment). The question was brought up weather or not we could use this 230V transformer to feed this 240V A/C unit. The A/C connection diagram did not show a neutral being used as part of the input connection and just required the two legs of 240V. It did show a ground connection on the input connection.
At first we thought about just using the 230V source to the A/C unit because there was no neutral needed. But then after seeing electronics in the unit I thought that maybe these electronics were designed to have a 120V L-G reference and if we brought in the 230V L-G source then they would not have this.
We called the A/C rep and he insisted that we must have the two seperate legs of 120V L-G brought to the unit to give the 240V. I questioned him on why this was since they did not have a neutral but he was not very clear in his answer. I can only assume that there were components inside that referened to ground. Is this a correct assumption?
If there were no electronics or anything inside that referenced to ground such as a motor, or heater, then would it have been o.k. to connect the 230V L-G supply to this unit and have it operate fine ( ignoring the slight volage difference).
At first we thought about just using the 230V source to the A/C unit because there was no neutral needed. But then after seeing electronics in the unit I thought that maybe these electronics were designed to have a 120V L-G reference and if we brought in the 230V L-G source then they would not have this.
We called the A/C rep and he insisted that we must have the two seperate legs of 120V L-G brought to the unit to give the 240V. I questioned him on why this was since they did not have a neutral but he was not very clear in his answer. I can only assume that there were components inside that referened to ground. Is this a correct assumption?
If there were no electronics or anything inside that referenced to ground such as a motor, or heater, then would it have been o.k. to connect the 230V L-G supply to this unit and have it operate fine ( ignoring the slight volage difference).