I'm wondering if a 24 VDC circuit supplied through a 2A glass fuse requires an EGC? Also what sections of the code support your claims one way or the other?
Welcome to the forum.
As we often like to do with such questions, first check Art. 250 and tell us what your deduction is.
Just curious, what is the application? Power source, wiring type, load, environment, etc.
Yes, and this a common misunderstand of the code that just because it is low voltage it is class 2. I see this with LED strip lighting that is only approved for class 2 and the installer thinks he can just use a giant driver that is not class 2 certified do to too much current and all is good.I used to automatically think all low voltage was class2, and most is, then I saw a communications equipment room that had a 20kVA 48VDC rectifier and the positive was the grounded conductor.
What is the current limit for 12v LED drivers to use cl-2 wiring?I see this with LED strip lighting that is only approved for class 2 and the installer thinks he can just use a giant driver that is not class 2 certified do to too much current and all is good.
The limit is that the power source has to be listed as class 2. And you cannot just put a 2a fuse on a 24 vdc circuit and call it class 2 wiring.What is the current limit for 12v LED drivers to use cl-2 wiring?