24 VDC, 2A circuit

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

As we often like to do with such questions, first check Art. 250 and tell us what your deduction is.

Just curious, what is the application? Power source, wiring type, load, environment, etc.
 
Location
Des Moines, IA
Occupation
Engineer
Welcome to the forum.

As we often like to do with such questions, first check Art. 250 and tell us what your deduction is.

Just curious, what is the application? Power source, wiring type, load, environment, etc.


Last posting has the following . . .

This subject actually attracted the attention of Mr. Holt himself. In a private discussion, he helped me see that the NEC does not require this 24 Volt system be grounded and therefore would not require an EGC for any part of the circuit.

Unfortunately I don't believe richwaskowitz is alive any longer to ask what specific sections of the code Mike Holt pointed out to him.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The NEC is considered "permissive" in the sense that something not specifically mandated nor prohibited is optional, meaning that an EGC is not required because it's not required or exceptions allow omitting it.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
I used to automatically think all low voltage was class2, and most is, then I saw a communications equipment room that had a 20kVA 48VDC rectifier and the positive was the grounded conductor.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I used to automatically think all low voltage was class2, and most is, then I saw a communications equipment room that had a 20kVA 48VDC rectifier and the positive was the grounded conductor.
Yes, and this a common misunderstand of the code that just because it is low voltage it is class 2. I see this with LED strip lighting that is only approved for class 2 and the installer thinks he can just use a giant driver that is not class 2 certified do to too much current and all is good.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I see this with LED strip lighting that is only approved for class 2 and the installer thinks he can just use a giant driver that is not class 2 certified do to too much current and all is good.
What is the current limit for 12v LED drivers to use cl-2 wiring?
 