240.100 Feeders and Branch circuits. (A)(1)

Status
Not open for further replies.

d-decherd

Member
Location
Illinois
Does anyone have a schematic of what is discussed in this article? I avoid 3 phase 3 wire Delta circuits as not being bonded and having a path for returning fault current. The equipment is severly damaged when a ground fault occures on an ungrounded system.What is residual current of current transformers? What is meant by where the neutral is not regrounded on the load side of the circuit?
 
Re: 240.100 Feeders and Branch circuits. (A)(1)

240.100(A)(1) is about ckt. bkr.OCP in medium voltage ckts.

The basic principles are the same as 600V. & below, in that conductors are protected against overcurrents. - However, a medium voltage ckt. bkr. is physically totally different than a typical 600V. & below bkr.

Instead of having "series trips", in which the load current passes through a tripping element, a medium voltage bkr. can be thought of as an electrically-operated switch with a close coil & a trip coil.

Protective relays (driven by the output of current transformers that monitor the load current) are used to energize the trip coil from a control circuit source. The control ckt. source is frequently DC from batteries.

There are common ways that these protective relays are connected.

These statements are a greatly simplified introduction to medium voltage ckt. bkrs.
OCP above 600V. is a subject in itself. You could even consider it a speciality.
Some rather intense engineering publications are available. The IEEE series of books & mfgr's. such as, Square D, Westinghouse/Cutler Hammer, ABB, Basler, etc. offer info on the subject.
 